on: March 06, 2011, 11:26:05 am » posted from:Taipei,T\'ai-pei,Taiwan

Three-phase electric power is a common method of alternating-current electric power generation, transmission, and distribution. A three-phase system is generally more economical than others because it uses less conductor material to transmit electric power than equivalent single-phase or two-phase systems at the same voltage.
In a three-phase system, three circuit conductors carry three alternating currents (of the same frequency) which reach their instantaneous peak values at different times. Taking one conductor as the reference, the other two currents are delayed in time by one-third and two-thirds of one cycle of the electric current. This delay between phases has the effect of giving constant power transfer over each cycle of the current and also makes it possible to produce a rotating magnetic field in an electric motor.
* V_a(t)=V_p \sin(\omega\,t-\tfrac{2}{3}\pi)=V_p (-\tfrac{1}{2}\sin \omega t-\tfrac{\sqrt{3}}{2}\cos\omega t)
* V_b(t)=V_p \sin(\omega\,t)
* V_c(t)=V_p \sin(\omega\,t+\tfrac{2}{3}\pi)=V_p (-\tfrac{1}{2}\sin \omega t+\tfrac{\sqrt{3}}{2}\cos\omega t)

And you will find V_a(t)+V_b(t)+V_c(t)=0.


Three-phase systems may have a neutral wire. A neutral wire allows the three-phase system to use a higher voltage while still supporting lower-voltage single-phase appliances.
The phase currents tend to cancel out one another, summing to zero in the case of a linear balanced load. This makes it possible to eliminate or reduce the size of the neutral conductor; all the phase conductors carry the same current and so can be the same size, for a balanced load.

Power transfer into a linear balanced load is constant, which helps to reduce generator and motor vibrations.

Three-phase systems can produce a magnetic field that rotates in a specified direction, which simplifies the design of electric motors.



The following simulation let you play with such 3 phase electric power system, power source and load either in Y or \Delta connection mode.
Use checkbox to select AC Y mode (AC \Delta mode) or R Y mode (R \Delta mode)
For AC Y mode:
Phase voltage referer to VRN=Va,VSN=Vb,VTN=Vc,
Line voltage referer to VRS=Va-Vb,VST=Vb-Vc,VTR=Vc-Va.

Y-connected sources and loads always have line voltages greater than phase voltages, and line currents equal to phase currents. If the Y-connected source or load is balanced, the line voltage will be equal to the phase voltage times the square root of 3.

V_a-V_b=V_p (-\tfrac{3}{2}\sin \omega t-\tfrac{\sqrt{3}}{2}\cos\omega t)=\sqrt{3}\,V_p (-\tfrac{\sqrt{3}}{2}\sin \omega t-\tfrac{1}{2}\cos\omega t)=\sqrt{3} V_p \sin(\omega\,t-\tfrac{5}{6}\pi)

Embed a running copy of this simulation

Embed a running copy link(show simulation in a popuped window)
Full screen applet or Problem viewing java?Add http://www.phy.ntnu.edu.tw/ to exception site list
Press the Alt key and the left mouse button to drag the applet off the browser and onto the desktop. This work is licensed under a Creative Commons Attribution 2.5 Taiwan License
  • Please feel free to post your ideas about how to use the simulation for better teaching and learning.
  • Post questions to be asked to help students to think, to explore.
  • Upload worksheets as attached files to share with more users.
Let's work together. We can help more users understand physics conceptually and enjoy the fun of learning physics!


* electronic_3phasepowerNload.gif (13.65 KB, 856x367 - viewed 695 times.)

* 3-phase_flow.gif (293.66 KB, 412x263 - viewed 1952 times.)

* 423px-CenterTappedTransformer.svg.png (44.96 KB, 423x436 - viewed 817 times.)

* 3phase-rmf-320x240-180fc.gif (216.42 KB, 320x240 - viewed 2533 times.)

* ejs_electronic_3phasepowerNloadYY.jpg (34.67 KB, 756x318 - viewed 2849 times.)

* ejs_electronic_3phasepowerNloadYD.jpg (35.96 KB, 756x318 - viewed 2682 times.)

* ejs_electronic_3phasepowerNloadDY.jpg (35.5 KB, 756x318 - viewed 2639 times.)

* ejs_electronic_3phasepowerNloadDD.jpg (36.96 KB, 756x318 - viewed 2650 times.)
Logged
Fu-Kwun Hwang
Administrator
Hero Member
*****
Offline Offline

Posts: 3080



WWW
«
Embed this message
Reply #1 on: March 13, 2011, 12:12:02 pm » posted from:Taipei,T\'ai-pei,Taiwan


V_{RS}=V_{12}=V_{RN}-V_{SN}, for root mean square value |V_{RS}|=\sqrt{3}|V_{RN}|
I_{10}=V_{RN}/R


V_{RS}=V_{12}=V_{RN}-V_{SN}, for root mean square value |V_{RS}|=\sqrt{3}|V_{RN}|

I_{12} =V_{RS}/R=(V_{RN}-V_{SN})/R,I_{23} =V_{ST}=(V_{SN}-V_{TN})/R, I_{31}= V_{TS}=(V_{TN}-V_{SN})/R
I_R=I_{12}-I_{31}= (V_{RN} -V_{SN})/R-(V_{TN}-V_{SN})/R =(2V_{RN} -V_{SN}-V_{TN})/R=3V_{RN}/R
 V_{RN}+V_{SN}+V_{TN}=0, I_S=3V_{SN}/R, I_T=3V_{TN}/R


V_{12}=V_{RS}
I_{RS} =V_{RS}/(3R),I_{ST} =V_{ST}/(3R),I_{TR} =V_{TR}/(3R)
I_1=I_{10}=I_{RS}-I_{TR} root mean square |I_{10}|=\sqrt{3} |I_{RS}|
I_{12}=I_{10}-I_{20} root mean square |I_{12}|=\sqrt{3} |I_{10}|=3 |I_{RS}|=|V_{RS}|/R


V_{12}=V_{RS}
I_{RS} =V_{RS}/R,I_{ST} =V_{ST}/R,I_{TR} =V_{TR}/R
I_{1}=I_{RS}-I_{TR} root mean square |I_{1}|=\sqrt{3} |I_{RS}|
I_2=I_{ST}-I_{RS} , I_3=I_{TR}-I_{ST}
Logged
ahmedelshfie
Ahmed
Hero Member
*
Offline Offline

Posts: 954



«
Embed this message
Reply #2 on: March 14, 2011, 08:47:30 am » posted from:Uberaba,Minas Gerais,Brazil

Very nice applet, great work prof  Wink
Logged
Pages: [1]   Go Up
  Print  
Give me a standpoint and I will move the earth. ...Archimedes (287-212BC)
 
Jump to:  


Related Topics
Subject Started by Replies Views Last post
Transformer without load
Electromagnetism
Fu-Kwun Hwang 0 14270 Last post June 08, 2008, 11:06:10 am
by Fu-Kwun Hwang
A loop rotating in a magnetic field (How electric power generator works!)
Electromagnetism
Fu-Kwun Hwang 5 50345 Last post December 12, 2009, 11:46:40 am
by Fu-Kwun Hwang
Power Loss in electric power transmission network .. V^2/R OR I^2*R?/board:37-100-
Question related to Physics or physics related simulation
hengleng 2 56017 Last post October 14, 2016, 06:41:10 pm
by Shahin1990
A loop rotating in a magnetic field (How electric power generator works!
electromagnetism
ahmedelshfie 7 7131 Last post April 22, 2010, 05:19:06 pm
by ahmedelshfie
Pendula in-phase and out-of-phase
Collaborative Community of EJS
LeeTl 1 6042 Last post May 23, 2013, 09:26:41 am
by lookang
Powered by MySQL Powered by PHP Powered by SMF 1.1.13 | SMF © 2006-2011, Simple Machines LLC Valid XHTML 1.0! Valid CSS!
Page created in 3.398 seconds with 22 queries.since 2011/06/15